header bg

Scan QR code or get instant email to install app

Question:

What is the minimum size of THWN conductors required for single phase 10 HP motor connected to 240 volts supply?

A 6 AWG THWN Copper
explanation

Refer: NEC Table 430.248
FLI current of single phase 10 HP motor at 230 volts = 50 amperes
Refer: NEC 430.22
Minimum conductor ampacity = 50 x 125% = 62.5 amperes
Refer: NEC Table 310.15(B)(16)
6 AWG THWN Copper with 65 amperes capacity at 75 degrees C is suitable conductor for the motor