What is the minimum size secondary conductor required for a 2 wire 480 volts/ 120 volts transformer rated at 2.3 KVA with 75 degrees C temperature at terminals?
A
14 AWG
explanation
Secondary transformer current = 2300 / 120 = 19.16 amperes Refer: NEC Table 310.15(B)(16) The suitable conductor is 14 AWG with 20 amperes capacity at 75 degrees C